[ClusterLabs] When does Pacemaker shoot other nodes in the head
Ken Gaillot
kgaillot at redhat.com
Fri Sep 9 14:46:55 UTC 2016
On 09/09/2016 08:52 AM, Auer, Jens wrote:
> Hi,
>
> a client asked me to describe the conditions when Pacemaker uses STONITH
> to bring the cluster into a known state. The documentation says that
> this happens when "we cannot establish with certainty a state of some
> node or resource", but I need some more concrete explanations.
> Specifically, he is wondering what happens when
> 1. a resource, e.g. a virtual ip, fails to often
> 2. the heartbeats of one of the cluster nodes are not received anymore
> 3. combinations of these two
>
> Is there some better definition of the conditions which trigger STONITH?
To state the obvious, just for completeness: Before stonith/fencing can
be used at all, stonith-enabled must be true, working fence devices must
be configured, and each node must be able to be targeted by at least one
fence device. If fence device failure is a concern, a fencing topology
should be used with multiple devices. The fencing setup should be
verified by testing before going into production.
Assuming that's in place, fencing can be used in the following situations:
* Most importantly, if corosync communication is broken between nodes,
fencing will be attempted. If no-quorum-policy=ignore, each partition
will attempt to fence the other (in two-node clusters, a fence delay is
commonly used on one node to avoid a death match here); otherwise, the
partition with quorum will try to fence the partition without quorum.
This can happen due to a node or nodes crashing, being under extreme
load, losing network connectivity, etc. Options in corosync.conf can
affect how long it takes to detect an outage, etc.
* If no-quorum-policy=suicide, and one or more nodes are separated from
the rest of the cluster such that they lose quorum, they will fence
themselves.
* If startup-fencing=true (the default), and some nodes are not present
when the cluster first starts, those nodes will be fenced.
* If a resource operation has on-fail=fence, and it fails, the cluster
will fence the node that had the failure. Note that on-fail defaults to
fence for stop operations, since if we can't stop a resource, we can't
recover it elsewhere.
* If someone/something explicitly requests fencing via the stonithd API
(for example, "stonith_admin -F <node>"), then of course the node will
be fenced. Some software, such as DRBD and DLM, can be configured to use
pacemaker's fencing, so fencing might be triggered by them under their
own conditions.
* In a multi-site cluster using booth, if a ticket constraint has
loss-policy=fence and the ticket is lost, the cluster will fence the
nodes that were running the resources associated with the ticket.
I may be forgetting some, but that's the most important.
How the cluster responds to resource-level failures (as opposed to
losing an entire node) depends on the configuration, but unless you've
configured on-fail=fence, fencing won't be involved. See the
documentation for the migration-threshold and on-fail parameters.
> Best wishes,
> jens
>
> --
> *Jens Auer *| CGI | Software-Engineer
> CGI (Germany) GmbH & Co. KG
> Rheinstraße 95 | 64295 Darmstadt | Germany
> T: +49 6151 36860 154
> _jens.auer at cgi.com_ <mailto:jens.auer at cgi.com>
> Unsere Pflichtangaben gemäß § 35a GmbHG / §§ 161, 125a HGB finden Sie
> unter _de.cgi.com/pflichtangaben_ <http://de.cgi.com/pflichtangaben>.
More information about the Users
mailing list