[Pacemaker] Problem with dual-PDU fencing node with redundant PSUs

Digimer lists at alteeve.ca
Wed Jun 26 15:52:00 EDT 2013


This question appears to be the same issue asked here:

http://oss.clusterlabs.org/pipermail/pacemaker/2013-June/018650.html

In my case, I have two fence methods per node; IPMI first with
action="reboot" and, if that fails, two PDUs (one backing each side of
the node's redundant PSUs).

Initially I setup the PDUs as action "reboot" figuring that the
fence_toplogy tied them together, so pacemaker would call "pdu1:port1;
off -> pdu2:port1; off; (verify both are off) -> pdu1:port1; on ->
pdu2:port1; on".

This didn't happen though. It called 'pdu1:port1; reboot' then
"pdu2:port1; reboot", so the first PSU in the node had it's power back
before the second PSU lost power, meaning the node never powered off.

So next I tried;

pdu1:port1; off -> pdu2:port1; off -> pdu1:port1; on -> pdu1:port1; on

However, this seemed to have actually done;

pdu1:port1; reboot -> pdu2:port1; reboot -> pdu1:port1; reboot ->
pdu1:port1; reboot

So again, the node never lost power to both PSUs at the same time, so
the node didn't power off.

This makes PDU fencing unreliable. I know beekhof said:

  "My point would be that action=off is not the correct way to configure
what you're trying to do."

in the other thread, but there was no elaborating on what *is* the right
way. So if neither approach works, what is the proper way for configure
PDU fencing when you have two different PDUs backing either PSU?

  I don't want to disable "reboot" globally because I still want the
IPMI based fencing to do action="reboot". If I just do "off", then the
node will not power back on after a successful fence. This is better
than nothing, but still quite sub-optimal.

-- 